hurk27
- Portage, Indiana NEC: 2008
Ryandumas
You have been given enough information to design this job. The conductor must have at least the ampacity of the 2000 amp breaker. I believe
1. You must get the local inspector involved
2. Will he allow the use of table 310.17 for this installation
3. If any of the conductors are in conduit the information given will not be valid.
4. How are you going to manage all of these conductors w/o conduit
5. If not in conduit does close grouping of the conductors require further adjustments
I think it was said this is on a barge, on the water, see post 1
so not in NEC territory I think?
also I would think the cable would have to be flexable fine stranded type hard use.