I am preparing for the Colorado State Licensing Examination and I am working on learning to solve the examples on the back of the 2005 NEC.
In Example D3, for a commercial building, the minimum size of the feeder is based on the sum of the noncontinuous load plus 125% of the continuous load (See the bottom left of page 70-719).
In Example D3(a), for an industrial installation, the minimum size of the feeder is based on the actual load, without the 125% factor applied to the continuous load (See the 6th line below the heading "Ungrounded Feeder Conductors" on page 70-720).
I can't find any section in the code that states that these two installations should be treated differently. Every section I read says that the procedure in Example D3 is the correct one.
Does anyone know why these two examples are solved differently?
Thanks
In Example D3, for a commercial building, the minimum size of the feeder is based on the sum of the noncontinuous load plus 125% of the continuous load (See the bottom left of page 70-719).
In Example D3(a), for an industrial installation, the minimum size of the feeder is based on the actual load, without the 125% factor applied to the continuous load (See the 6th line below the heading "Ungrounded Feeder Conductors" on page 70-720).
I can't find any section in the code that states that these two installations should be treated differently. Every section I read says that the procedure in Example D3 is the correct one.
Does anyone know why these two examples are solved differently?
Thanks