On a new home, I spoke with the HVAC company to verify the amperage of the equipment the were providing. Everything was fine except one minor detail. The Trane unit in the attic was to be 40 amps. I ran 8/2. When I was sticking the wire into the machine yesterday, I read the data plate. It reads the minimum ampacity is 45 amps, minimum and maximum breaker is 45 amps. I know NM is rated at 90 degrees (45 amps), but the breaker being 75 degrees knocks it down to 75 degrees (40 amps). The actual load is 32 amps for the heat strips and 4.3 amps for the fan motor.
Any input (such as something I have missed in the code) or should I just run new #6 wire and duke it out with the HVAC company? (The info was actually written on a stud and there may be a picture, and the HO witnessed it all as he is owner/builder)
Thanks,
c2500
Any input (such as something I have missed in the code) or should I just run new #6 wire and duke it out with the HVAC company? (The info was actually written on a stud and there may be a picture, and the HO witnessed it all as he is owner/builder)
Thanks,