I ran into an interesting situation this week, and found my knowledge of theory lacking a bit.
The one-line is as follows:
-Service Disconnect A-
Large service, 3/? 120/208Y, say 600 or 800A, serving 10 apartment units. This service is connected to building steel, building steel has a bonding jumper to water pipe; service is also connected to ground rod.
-Service Disconnect B-
Same utility transformer supplies a CT can, nippled to a 400A 120/208Y disconnect serving house loads. It is a few inches away from the residential service. It has a GEC running to building steel.
-Service Disconnects C & D-
From Service B's CT can, there is an underground run into a gutter inside the Fire Riser room. There will be a disconnect for a 60 HP Fire Pump and a 2 HP Jockey Pump in the riser room.
Problem: The underground conduit run to C & D was accidentally undersized. The installer was going to compensate by running three phase conductors to the gutter, omitting the neutral, and then connecting service disconnects C & D to building steel.
When I tried to explain the problem (beyond simply saying it ain't code ), I found myself grasping at what would transpire if a ground fault were to occur in the Fire Pump. In previous discussions here, I know that the path away from the phase conductors, through building steel to the CT can would present a higher impedance to the fault, but had a hard time attaching numbers and explaining the concept to my satisfaction. Who can help me out here?
(The neutral will be present in the underground when this gets pulled in, I succeeded - I am just looking for a better explanation of the numbers and the theory.)
Thanks in advance.
The one-line is as follows:
-Service Disconnect A-
Large service, 3/? 120/208Y, say 600 or 800A, serving 10 apartment units. This service is connected to building steel, building steel has a bonding jumper to water pipe; service is also connected to ground rod.
-Service Disconnect B-
Same utility transformer supplies a CT can, nippled to a 400A 120/208Y disconnect serving house loads. It is a few inches away from the residential service. It has a GEC running to building steel.
-Service Disconnects C & D-
From Service B's CT can, there is an underground run into a gutter inside the Fire Riser room. There will be a disconnect for a 60 HP Fire Pump and a 2 HP Jockey Pump in the riser room.
Problem: The underground conduit run to C & D was accidentally undersized. The installer was going to compensate by running three phase conductors to the gutter, omitting the neutral, and then connecting service disconnects C & D to building steel.
When I tried to explain the problem (beyond simply saying it ain't code ), I found myself grasping at what would transpire if a ground fault were to occur in the Fire Pump. In previous discussions here, I know that the path away from the phase conductors, through building steel to the CT can would present a higher impedance to the fault, but had a hard time attaching numbers and explaining the concept to my satisfaction. Who can help me out here?
(The neutral will be present in the underground when this gets pulled in, I succeeded - I am just looking for a better explanation of the numbers and the theory.)
Thanks in advance.