Need Help Understanding the Code

Status
Not open for further replies.

czars

Czars
Location
West Melbourne, FL
Occupation
Florida Certified Electrical Contractor
In the 2014 NEC I understand that Chapters 1-4 apply generally to all electrical installations and that Chapter 5 modifies Chapters 1-4. My question concerns the requirement for GFCI and AFCI protection for Mobile and Manufactured homes.

Article 210.8 contains the requirements for GFCI protection. However, Article 550.13(B) identifies the requirements for GFCI installations in Mobile and Manufactured homes. I assume from this that only the GFCI installations identified in Article 550.13(B) are required for Mobile and Manufactured homes. Is this a correct assumption??

Article 210.12 identifies the requirements for AFCI protection in homes. However, it appears that Article 550 does not address requirements for AFCi protection in Mobile and Manufactured home. Does this mean that there are no requirements for AFCI protection or does it mean that since Article 550 contains no modifications to Article 210.12, all of Article 210.12 applies to Mobile and
 
Thanks for your reply. I didn't look for the requirement to be located following Outdoor outlets, A/C equipment, etc.
 