need help with CSA codes in regards to GFCI/conduit requirements 120/240VAC breaker box

emiller233

Senior Member
Location
pittsburgh, pa
Occupation
Controls-Automation engineer
I'm not familiar at all with the CSA code, so I'm looking for some guidance on how to properly install this setup. I'm not sure what does/doesn't need GFCI breakers, or if I can just get away with GFCI receptacles and use standard breakers for everything.
  1. industrial application (Hydraulic power unit)
  2. outdoor rated box, but will be mounted inside of a shipping container so the entire system is 'portable'
    1. Does this have to be done on conduit or LFMC? or can we run cables in a wire tray?
      1. any requirements for CSA that I don't know about? I'm assuming we have to use rainttight fittings if we use EMT?
      2. does the conduit/LFMC need to be CSA stamped or anything?
  3. all single-phase 120VAC loads:
    1. 15A power to a cUL508A-rated industrial control panel (PLC and control stuff)
    2. 2500W immersion heater (hydraulic oil)
    3. 500W immersion heater (hydraulic oil)
    4. 500W immersion heater (hydraulic oil)
    5. (2) LED work lights mounted on the ceiling
    6. (2) 120VAC receptacles mounted on the interior walls
      1. are 'in-use' receptacle covers required? or can we use the spring-loaded door type?
 
The best guys to ask would be the guys building skids for the oil patch since this would be their bread and butter.

I don’t have a ton of experience so I couldn’t tell you with any real certainty one way or another.

I would think it might depend on if the unit is being connected to the grid. If it’s getting a meter base then everything would need to follow CEC. If the skid is being build as a piece of portable equipment then it’s possible it might fall under another other certifications.

I tray is fine as long as the cables weren’t liable to shift or move during transportation.

Is this a temporary setup or something that’s going to be dragged around and worked hard for the next 30 years?

If it were me I’d be using:
- Teck90 with proper teck connectors.
- Nema 4 or 4x enclosures and fs boxes.
- Cast weather proof cover plates. I think the plastic in use covers would get annihilated.

Looks like Home Depot sells an inexpensive Siemens 1ph 8cct outdoor panel board.
Model number: W0816ML1125.

I’m curious to know what everyone else thinks.