Motor load feeder calculations
Question: service feeder multimotor connection
460v service
1ea 120v 19.92amp continuous duty motor
1ea 230v 33.2amp 5 min. intermitten duty motor
1ea 230v 23.24amp continuous duty motor
1ea 460v 22.41amp continuous duty motor
1ea 460v 11.62 5 min. intermitten duty motor
1ea 460v 43.16amp continuous duty motor
I would first convert all the amperage rating to va using their voltages perspectively
Apply the derating of 85% to the 5min intermitten duty motors
Apply 125% to the highest load rated moter
2390.4va @ 100% = 2390.4va
7636va @ 85% = 6490.6va
5345va @ 100% = 5345va
10308.6va @ 100% = 10308.6va
5345.2va @ 85% = 4543.42va
19853.6va @ 125% = 24817va
total va = 53895.02
53895va / 460v = 117 amps