I’m installing a service for a new car wash. The car wash came with prints for the wiring for the car wash itself but not for the service. The building was previously a car wash but now they are installing a bigger system.
The service is 480 volt three phase. The installer wants a 400 amp breaker for his motor control center, a 200 amp breaker for a 480/277 200 amp panel and another 200 amp breaker for a step down transformer.
The total connected load is 318 amps, and the total building will be 352kw. I sent this to the power company and they said the most they will give me is 400 (320) amp meter system.
I have to put a 400 amp disconnect before and after the meter to satisfy the power company.
All that being said my question is do you think I can feed a 400 amp indoor panel board and put in a 400 breaker for the motor control center and the two 200 amp breaker? Or should I go to the 600 amp panel board ? If I go to the 600 amp then I have to feed it with bigger wire when it is still fused at 400 amps at the disconnect.
Any help would be appreciated.
I really don’t want to pay an engineer
The service is 480 volt three phase. The installer wants a 400 amp breaker for his motor control center, a 200 amp breaker for a 480/277 200 amp panel and another 200 amp breaker for a step down transformer.
The total connected load is 318 amps, and the total building will be 352kw. I sent this to the power company and they said the most they will give me is 400 (320) amp meter system.
I have to put a 400 amp disconnect before and after the meter to satisfy the power company.
All that being said my question is do you think I can feed a 400 amp indoor panel board and put in a 400 breaker for the motor control center and the two 200 amp breaker? Or should I go to the 600 amp panel board ? If I go to the 600 amp then I have to feed it with bigger wire when it is still fused at 400 amps at the disconnect.
Any help would be appreciated.
I really don’t want to pay an engineer