Re: Need help with procedure for testing impedance of a dist
The transformer is rated 1000 kVA, 480 secondary volts, 5.75% impedance.
Rated full load amp output of the transformer is
1000 kVA / (480 x 1.732) = 1203 amps
The 5.75% impedance rating indicates that 1203 amps will flow in the secondary if
the secondary is short circuited line to line and the primary voltage is raised from
zero volts to a point at which 5.75% of 480 volts, or, 27.6 volts, appears at the
secondary terminals. Therefore, the impedance (Z) of the transformer secondary may
now be calculated:
Z = V / I = 27.6 volts / 1203 amps = .02294 ohms
The transformer is connected directly to the utility power lines which we will
assume are capable of supplying the transformer with an unlimited short circuit
kVA capacity. The utility company will always determine and advise of the short
circuit capacity available at any facility upon request.
With unlimited short circuit kVA available from the utility, the short circuit
amperage capacity which the transformer can deliver from its secondary is
480 volts / .02294 = 20,924 amps
This is for example only.