Was asked this question and need some help to answer.
Primary side is 480v
Secondary side is 240v
Secondary panel is 200amp 3 phase
I need to determine the kVA rating of transformer and the conductor size for both the primary side and secondary side.
Here is what I did.
Since we have a 200 amp panel I took the 240*1.732*200 which gave me 84 kva which next size transformer is 100kva.
Then on primary side I took 100kva divided by 480*1.732 which gave me 120 amps. 120*125% is 150 amps 1/0 cu conductor.
On secondary side I divided 100kva by 240*1.732 which gave me 240.8 amps. 240.8 *125% is 301 amps 350 kcmil conductor.
350 kcmil conductor seems to large for this application. So It seems I'm not calculating something correctly.
Also does the 200 amp panel need to be sized down 80%. Making it 160 amps full load.
Thanks for any help.