All right guys, here it is;;
One of my jobs has an interesting situation. An inspector has made a call which I think is incorrect. He says that my 200-amp Cutler Hammer subpanel's 10k AIC rating must match my 1200-amp RSE Sierra switch gear's 42 AIC rating...even though I am feeding the subpanel with 200-amp type T fuses. My understanding of the code is that if type T fuses are used the AIC rating is good from 10K to 200K. Am I wrong?
Thanks,
Salty Flicker
One of my jobs has an interesting situation. An inspector has made a call which I think is incorrect. He says that my 200-amp Cutler Hammer subpanel's 10k AIC rating must match my 1200-amp RSE Sierra switch gear's 42 AIC rating...even though I am feeding the subpanel with 200-amp type T fuses. My understanding of the code is that if type T fuses are used the AIC rating is good from 10K to 200K. Am I wrong?