my employer wants me to move an exterior 3phase 208Y/120 service panel to the inside of a control cabinet. the only option I see is to use fuses for the main supply leads. What sized fuses do I need for each leg? the existing panel is rated for 125Amps.
 
At face value this seems really odd. Can you add more detail?

Reminder that service disconnects need to be service rated.
 
The service is a 4 wire 208Y going to a service panel feeding about 8 circuits. I ordered a 18 circuit bus that can be mounted inside the control cabinet that allows you to attached single double or 3 pole miniature breakers to it rated for 80A. I'm thinking g this should do the trick. I want to put a service disconnect before the bus. Should I make it an 80A breaker also or should it be larger?
 