Oakey
Senior Member
- Location
- New Jersey
I need some help guys,I went to a service call tonite for flickering lights in a house. When the microwave was being used the lights would dim, the circuit was one of the ones controlling most common areas of the house. I measured 25 amps on the circuit notably on a Federal panel 20 amp breaker. Opening up a junction box near the panel for the same circuit I could see that it was burnt and darn well hot to the touch. Out of the 3 leads out of this JB one was unusable as I stripped the insulation back almost 4 feet on the old BX to find it still dry and burnt and it was converted to 15 amp at this point. I have to rerun a new wire to replace it, hopefully not to far ... Maybe megger it?
Here is my question finally:
This Federal panel actually looked fairly new and with new breakers also, obviously this this shoud've tripped. Was there ever a newer Federal that was safe to use? These ppl just bought the house and I dont want to stir up a bees nest without accurate info about these panels. Gotta love the reds as ground...Btw the neutrals are in the panel above..
Here is my question finally:
This Federal panel actually looked fairly new and with new breakers also, obviously this this shoud've tripped. Was there ever a newer Federal that was safe to use? These ppl just bought the house and I dont want to stir up a bees nest without accurate info about these panels. Gotta love the reds as ground...Btw the neutrals are in the panel above..