garnerm
Member
- Location
- Montgomery, AL
I designed a 208V panel to be feeded from a dry type transformer which is feeded from a 480V panel in the same elec. room. I sized the ground for the transformer to the panel on the secondary side via the equipment grounding table 250.122 in the NEC. My city electrical inspector said that the ground needs to be sized via the service entrance table 250.66. I think this is BS. has anybody ever run into this issues and if so how did you deal with it? Also, if you think he is right please explian why, and if not please help me figure out some key points in the code where I can build a case. Thanks for your help.
PS, I know this shouldn't be a service entrance ground because we are not changing buildings, this is in the same building, even the same room.
PS, I know this shouldn't be a service entrance ground because we are not changing buildings, this is in the same building, even the same room.