Need Help

Status
Not open for further replies.

bkg

Member
I've got 12 2x4 Lay in's on a 20 amp circuit controlled by a 3 way switch. I'm getting excessive heat along the entire circuit especially from the travelers (12/3) I know there is not a set max length ( per NEC ) for wire but I've got about 230 feet of #12 in this circut.Any Ideas?
 
Re: Need Help

What is the total load on the circuit?

If these are older 4 lamp T-12 fixtures @ 120 volts that is a maxed out circuit.

What do you consider excessive heating?

Warm is not bad. :)
 
Re: Need Help

BKG-look at the ballast amps, multiply by 2 per fixure and x 12 fixtures. The limit for a 20 amp ckt is 80% or 16 amps. You have to take the ballast amps as it includes the losses in the ballast. An easy fix is to replace the ballasts with T-8's and new lamps.
 
Re: Need Help

Well that would explain where I mis-calculated...
.75 amp per ballast puts me at 18 amps.There are actually 3 circuits like this. I'm thinking perhaps pulling 2 lights off each circuit and running a 4th circuit of 6. Have to change out the boxes,add wire, 1/2 day. Ahh*#$@ :roll:
Thanks for the help... any idea what a T8 ballast runs ( $$ ) these days?
 
Re: Need Help

just paid 20.75 for each Advance 4P32SC35I electronic ballast. That was not a quantity price.
1.32 for each GE F34CW T-8 lamp. Non-quantity price also.
 
Re: Need Help

In some states (as in Washington) the use of T-8 & electronic ballasts is required by an energy code. However, I can get a rebate from our POCO on a retrofit, and you energy savings will give you a pretty good payback, plus the light quality is better (3500 deg K or higher) and there is no lamp flicker.
 