Re: Need Neutral from 3 Phase Grounded Delta
240.85 Applications. A circuit breaker with a straight voltage rating, such as 240V or 480V, shall be permitted to be applied in a circuit in which the nominal voltage between any two conductors does not exceed the circuit breaker?s voltage rating. A two-pole circuit breaker shall not be used for protecting a 3-phase, corner-grounded delta circuit unless the circuit breaker is marked 1?3 to indicate such suitability.
A circuit breaker with a slash rating, such as 120/240V or 480Y/277V, shall be permitted to be applied in a solidly grounded circuit where the nominal voltage of any conductor to ground does not exceed the lower of the two values of the circuit breaker?s voltage rating and the nominal voltage between any two conductors does not exceed the higher value of the circuit breaker?s voltage rating.
FPN
roper application of molded case circuit breakers on 3-phase systems, other than solidly grounded wye, particularly on corner grounded delta systems, considers the circuit breakers? individual pole-interrupting capability.
From the NFPA Handbook
A circuit breaker marked 480Y/277V is not intended for use on a 480-volt system with up to 480 volts to ground, such as a 480-volt circuit derived from a corner-grounded, delta-connected system. A circuit breaker marked either 480V or 600V should be used on such a system. In like manner, a circuit breaker marked 120/240V is not intended for use on a delta-connected 240-volt circuit. A 240-volt, 480-volt, or 600-volt circuit breaker should be used on such a circuit. The slash (/) between the lower and higher voltage ratings in the marking indicates that the circuit breaker has been tested for use on a circuit with the higher voltage between phases and with the lower voltage to ground.