Re: Need to size parallel service
Re: Need to size parallel service
Originally posted by manny:
Question ? If i have a 400 amp Meter Can i Parallel from that meter with Two diffrent size wire....let say 3-1/0wire and 3-3/0wire..OR do I need a gutter to make taps.. any one what do i need to make right....
Manny,
I do not understand what you are asking
Are you talking about runing from the 400 amp meter can to one 400 amp panel?
In this case the answer would be no you can not mix wire sizes 310.4 Conductors in Parallel as already said.
Or are you coming from the 400 amp meter can to two seperate panels, this is not Conductors in Parallel. In this case you could run differnt size conductors, based on load or OCPD
If you post more info it would help.
Bob