Re: Need to size parallel service
Re: Need to size parallel service
Manny If you are trying to run parallel conductors from the meter pan to service equipment then the code say's they must be the same size,lenght,and of the same material (cu or al)
310.4 Conductors in Parallel.
Now if you are trying to make a service entrance tap you can as long as the conductors dont enter a building more than what it takes to go to the main breaker and can be sized to the load or main breaker that they will feed.
230.40 Number of Service-Entrance Conductor Sets.
VII. Service Equipment ? Overcurrent Protection
230.90 Where Required.
In general 230 need to be read throughly