Needing Burial Cable in Wet Location

Status
Not open for further replies.

jgeo1123

New member
If provided a conduit under slab to a front counter in a retail store is this considered a wet location will burial cable be required.
 
Welcome to the forum.:)

Yes, a raceway underground is considered a wet location, and the conductors or cables installed in the raceway must be listed for use in a wet location. Take a look at 300.5(B) in the 2008 NEC.

Chris
 
Welcome to the forum! :smile:
If provided a conduit under slab to a front counter in a retail store is this considered a wet location will burial cable be required.
Not necessarily a direct-bury cable, but the conductors must be rated for wet locations, meaning a W in the type.
 