J jgeo1123 New member Jul 1, 2009 #1 If provided a conduit under slab to a front counter in a retail store is this considered a wet location will burial cable be required.
If provided a conduit under slab to a front counter in a retail store is this considered a wet location will burial cable be required.
raider1 Senior Member Staff member Location Logan, Utah Jul 1, 2009 #2 Welcome to the forum. Yes, a raceway underground is considered a wet location, and the conductors or cables installed in the raceway must be listed for use in a wet location. Take a look at 300.5(B) in the 2008 NEC. Chris
Welcome to the forum. Yes, a raceway underground is considered a wet location, and the conductors or cables installed in the raceway must be listed for use in a wet location. Take a look at 300.5(B) in the 2008 NEC. Chris
raider1 Senior Member Staff member Location Logan, Utah Jul 1, 2009 #3 I just noticed that this was posted in the low voltage forum. What type of system is this raceway for? Chris
I just noticed that this was posted in the low voltage forum. What type of system is this raceway for? Chris
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Jul 2, 2009 #4 Welcome to the forum! :smile: jgeo1123 said: If provided a conduit under slab to a front counter in a retail store is this considered a wet location will burial cable be required. Click to expand... Not necessarily a direct-bury cable, but the conductors must be rated for wet locations, meaning a W in the type.
Welcome to the forum! :smile: jgeo1123 said: If provided a conduit under slab to a front counter in a retail store is this considered a wet location will burial cable be required. Click to expand... Not necessarily a direct-bury cable, but the conductors must be rated for wet locations, meaning a W in the type.