wyopokesfan
- Saratoga, WY, USA
I recently noticed we had a drop in voltage across the entire saw mill where I work. Am relatively new here but think the loaded voltage here was close to 480V. Contacted a former electrician here and he agreed. We are fed from one feed of the power company to two 2500KVA transformers. One part of our facility coming off of transformer 1 is normal voltage, 480-482V loaded. Every MCC in the mill coming off of transformer 2 is 458-462Vphase to phase, loaded (running full production). The voltage coming out of the transformer is only 467 phase to phase loaded. All phases are withing a couple volts of each other and also within a couple volts all three phases to neutral (264-267V). Went through every MCC this morning on the main breakers and every large motor with 3 amp clamps, no real current imbalance or voltage imbalance anywhere. Could something in the mill be drawing the voltage down? Or possibly the transformer going bad? I know I can re-tap the transformer to get more out of it, but that does not explain the loss. I do not have CT's big enough to go around all 12 paralleled conductors on each phase coming from transformer. Also do not know of any metering devices in the mill to show me what the incoming voltage, current, etc. are. Any ideas would be greatly appreciated. Since I noticed the drop, we have had numerous 480V circuit breakers trip in random locations throughout the mill.