Help me understand negative sequence overcurrent elements.
I've recently taken over an account that uses methane from a landfill to generate power that they sell to the utility. The main breaker that connects this generation to the utility grid is protected with a SEL 351 protection relay.
They had this protection relay replaced a few months before we took over the account by another company. After a recent downstream fault, they were unable to bring one of their generators online as it would cause the negative sequence overcurrent element to assert and shut the whole facility down.
Working with a support engineer at SEL and digging through the manual, I discovered that a delay was recommended with this element to prevent transients from closure events causing nuisance trips. I added a 1.5 cycle delay and got them up and running.
A couple of weeks ago they called me again as they had experienced another trip event. The logs show that the reverse directional element was asserted. They were able to reset and be back in business, but want to eliminate these nuisance trips. SEL has been very helpful and tell me that these elements are set to default values and are working on getting recommendations for setting this up correctly.
I'm sure SEL will be able to help get this running, but this is new territory for me and I'd like to understand it better. Any of you utility or industrial guys able to explain how this works?
I get that it has to do with the voltage to current lead or lag, but I'm unclear on exactly how the values are derived and what typical setups look like. The manual is quite cryptic, any of you guys good at putting this in plain english?
Sent from my SM-A102U using Tapatalk
I've recently taken over an account that uses methane from a landfill to generate power that they sell to the utility. The main breaker that connects this generation to the utility grid is protected with a SEL 351 protection relay.
They had this protection relay replaced a few months before we took over the account by another company. After a recent downstream fault, they were unable to bring one of their generators online as it would cause the negative sequence overcurrent element to assert and shut the whole facility down.
Working with a support engineer at SEL and digging through the manual, I discovered that a delay was recommended with this element to prevent transients from closure events causing nuisance trips. I added a 1.5 cycle delay and got them up and running.
A couple of weeks ago they called me again as they had experienced another trip event. The logs show that the reverse directional element was asserted. They were able to reset and be back in business, but want to eliminate these nuisance trips. SEL has been very helpful and tell me that these elements are set to default values and are working on getting recommendations for setting this up correctly.
I'm sure SEL will be able to help get this running, but this is new territory for me and I'd like to understand it better. Any of you utility or industrial guys able to explain how this works?
I get that it has to do with the voltage to current lead or lag, but I'm unclear on exactly how the values are derived and what typical setups look like. The manual is quite cryptic, any of you guys good at putting this in plain english?
Sent from my SM-A102U using Tapatalk