I am trying to figure out how to arrive at the value set for negative sequence voltage

The software set a trigger value of 19.05 kV over voltage on the negative sequence voltage -- Please see attached .. how can I read this?

Thanks,
 

Attachments

  • V-.jpg
    V-.jpg
    18.6 KB · Views: 1

Ingenieur

Senior Member
Location
Earth
is that a fault or switching transient?
ground fault?
they look like pos seq voltages
under no fault the neg seq will be ~ 0
graph is hard to read


my guess
do you understand symmetrical components?
basically if you have a phase fault (vs ground fault) you will have neg seq current flow
if your normal phase seq is abc, you will have current with seq acb
if this results in a voltage > than 19.05 your relay trips
looks like system v is 132 kv?
 

junkhound

Senior Member
Location
Renton, WA
Occupation
EE, power electronics specialty
Paper or electronic strip chart?

You need to get an accurate phase differential to get negative anzero sequence values. Best to do with electronic cursor, a paper graph if that is what is shown takes some good eyeballing with sharp pencil and scale.

positive and negative sequence are exactly 120 deg apart, vecotor sums (plus zero sequence) = what you actually have. My old eyes see very little phase separation imbalance in the chart shown.
 

Besoeker

Senior Member
Location
UK
I am trying to figure out how to arrive at the value set for negative sequence voltage

The software set a trigger value of 19.05 kV over voltage on the negative sequence voltage -- Please see attached .. how can I read this?

Thanks,
I'm with the others. It doesn't look like negative sequence.
 

Ingenieur

Senior Member
Location
Earth
Paper or electronic strip chart?

You need to get an accurate phase differential to get negative anzero sequence values. Best to do with electronic cursor, a paper graph if that is what is shown takes some good eyeballing with sharp pencil and scale.

positive and negative sequence are exactly 120 deg apart, vecotor sums (plus zero sequence) = what you actually have. My old eyes see very little phase separation imbalance in the chart shown.

I think that is a model output
can't read the scales though
looks like a phase fault is initiated...first discontinuity
resulting in a neg seq v
which opens the cb resulting in a transient over-voltage
 

Ingenieur

Senior Member
Location
Earth
when transformed from the seq to the ph domain the neg seq (or zero seq) components can add (or subtract) to the ph domain magnitude

so even though we are looking at the ph seq magnitude the neg seq can increase it
the phase is basically the sum of the pos, neg and 0 seq after a ph shift transform matrix is applied
(the inverse of the one used to extract the 3 seq components from the ph domain)

the grads look like 20k
and the fault looks like 2.4 grads or 48k
this imo is the neg seq contribution
ref to rms and gnd = 48000/(sqrt 2 x sqrt3) ~ 19.5 kv
 
Last edited:

alsafaj

Member
Location
Dubai, UAE
when transformed from the seq to the ph domain the neg seq (or zero seq) components can add (or subtract) to the ph domain magnitude

so even though we are looking at the ph seq magnitude the neg seq can increase it
the phase is basically the sum of the pos, neg and 0 seq after a ph shift transform matrix is applied
(the inverse of the one used to extract the 3 seq components from the ph domain)

the grads look like 20k
and the fault looks like 2.4 grads or 48k
this imo is the neg seq contribution
ref to rms and gnd = 48000/(sqrt 2 x sqrt3) ~ 19.5 kv

I am going to share better resolution pics..
This is a disturbance recorder system -- monitoring the analog and binary inputs of a 132 kV line. See that a negative sequence voltage trigger is set to 19.05 kV --

Neg. seq.jpg
Looking at the graphs -- the voltage sequence and current sequence are maintained except for phase B-N the magnitude has changed.

V-2.jpg

See more:
V-3.jpg

V-4.jpg
 

Ingenieur

Senior Member
Location
Earth
thanks
the rotation will not change
the neg seq components will add to the pos seq and increase their magnitude

the blue trace
using the cursor
what is the pre fault magnitude
and the magnitude of the first 'spike'
I bet ~46.7 kv difference
 

Ingenieur

Senior Member
Location
Earth
Alsafa...

For voltage values on chart, calculated Neg-Seq is 23.3 kV, which is above the trip set-point! What are you questioning?

Regards, Phil Corso

I come up with +/- 20 kv
regardless
I think he wanted to understand
where did the trip of 19.05 come from
and how a neg seq component impacts the measured pos seq
 

alsafaj

Member
Location
Dubai, UAE
thanks
the rotation will not change
the neg seq components will add to the pos seq and increase their magnitude

the blue trace
using the cursor
what is the pre fault magnitude
and the magnitude of the first 'spike'
I bet ~46.7 kv difference

Pre-fault is set to 100ms and fault is 2 secs
Vb-n is 107.7 kV -- spike is ~ 156.2
Delta is ~ 48.70 kV
 

Ingenieur

Senior Member
Location
Earth
Pre-fault is set to 100ms and fault is 2 secs
Vb-n is 107.7 kV -- spike is ~ 156.2
Delta is ~ 48.70 kV

156.2 - 107.7 ~ 48.5
normalized to rms and ph-n ~ 19.8 > 19.05 so tripped
I hope we answered your questions
these are good primers on sym comp
https://cdn.selinc.com/assets/Liter...etrical-Pt1_AR_20130422.pdf?v=20170713-070622

https://www.gegridsolutions.com/smartgrid/Dec07/7-symmetrical.pdf

look at equation set 4 in first link
you can see ph a (v or i) = sum of seq comp = 0 seq + pos seq + neg seq

what this means is when you have a ph-ph fault neg seq components are created
these increase the summed measured value
 
Last edited:

alsafaj

Member
Location
Dubai, UAE
156.2 - 107.7 ~ 48.5
normalized to rms and ph-n ~ 19.8 > 19.05 so tripped
I hope we answered your questions
these are good primers on sym comp
https://cdn.selinc.com/assets/Liter...etrical-Pt1_AR_20130422.pdf?v=20170713-070622

https://www.gegridsolutions.com/smartgrid/Dec07/7-symmetrical.pdf

look at equation set 4 in first link
you can see ph a (v or i) = sum of seq comp = 0 seq + pos seq + neg seq

what this means is when you have a ph-ph fault neg seq components are created
these increase the summed measured value

Ah, got it. I understand now. Thank you!
 