I'm with the others. It doesn't look like negative sequence.I am trying to figure out how to arrive at the value set for negative sequence voltage
The software set a trigger value of 19.05 kV over voltage on the negative sequence voltage -- Please see attached .. how can I read this?
Thanks,
Paper or electronic strip chart?
You need to get an accurate phase differential to get negative anzero sequence values. Best to do with electronic cursor, a paper graph if that is what is shown takes some good eyeballing with sharp pencil and scale.
positive and negative sequence are exactly 120 deg apart, vecotor sums (plus zero sequence) = what you actually have. My old eyes see very little phase separation imbalance in the chart shown.
when transformed from the seq to the ph domain the neg seq (or zero seq) components can add (or subtract) to the ph domain magnitude
so even though we are looking at the ph seq magnitude the neg seq can increase it
the phase is basically the sum of the pos, neg and 0 seq after a ph shift transform matrix is applied
(the inverse of the one used to extract the 3 seq components from the ph domain)
the grads look like 20k
and the fault looks like 2.4 grads or 48k
this imo is the neg seq contribution
ref to rms and gnd = 48000/(sqrt 2 x sqrt3) ~ 19.5 kv
Alsafa...
For voltage values on chart, calculated Neg-Seq is 23.3 kV, which is above the trip set-point! What are you questioning?
Regards, Phil Corso
thanks
the rotation will not change
the neg seq components will add to the pos seq and increase their magnitude
the blue trace
using the cursor
what is the pre fault magnitude
and the magnitude of the first 'spike'
I bet ~46.7 kv difference
I come up with +/- 20 kv
regardless
I think he wanted to understand
where did the trip of 19.05 come from
and how a neg seq component impacts the measured pos seq
Pre-fault is set to 100ms and fault is 2 secs
Vb-n is 107.7 kV -- spike is ~ 156.2
Delta is ~ 48.70 kV
156.2 - 107.7 ~ 48.5
normalized to rms and ph-n ~ 19.8 > 19.05 so tripped
I hope we answered your questions
these are good primers on sym comp
https://cdn.selinc.com/assets/Liter...etrical-Pt1_AR_20130422.pdf?v=20170713-070622
https://www.gegridsolutions.com/smartgrid/Dec07/7-symmetrical.pdf
look at equation set 4 in first link
you can see ph a (v or i) = sum of seq comp = 0 seq + pos seq + neg seq
what this means is when you have a ph-ph fault neg seq components are created
these increase the summed measured value