When is the Neher and McGraft required to be used for 480V buried circuits? Is it limited to concrete encased ducts only? Does it apply to ducts in direct buried without concrete?
Whether it is "required" is a bit of an interpretation for the designer.The Neher McGrath calculation method can be used for any underground installation. But I believe it is never "required." There are other methods of determining ampacity. Two notes:
1. If you wish to use this method, the calculation must be performed by, and sealed by, a licensed Professional Engineer.
2. My memory of past attempts to use this method tells me that it will generally give you a lower ampacity value than the NEC tables. There is sometimes a question as to whether the tables can be used in a given situation.
Out of curiosity, may I ask whether you are already using this method, and if so, how? Or is your concern that you may be required to use it for a project, but you don't know how to use it?When is the Neher and McGraft required . . . ?
We are working on a project where the design engineer used the Neher and McGraft method for sizing the service for a 3000 KVA transformer. They came up with 13 - 750 KCMIL conductors per phase. The size of conductors makes for a difficult installation. We are trying to verify if the equipment is available to be provided with 13 lugs per phase. When we questioned the engineer, he is uneasy having gone this route but was questioned by 3rd party project reviewer to use the Neher and McGraft method. We would normally use 11 - 500 KCMIL conductors on a 4000 amp service. I am trying to verify the need of using the Neher and McGraft method.Out of curiosity, may I ask whether you are already using this method, and if so, how? Or is your concern that you may be required to use it for a project, but you don't know how to use it?
The tables in Annex B were made code text in the first draft, a number of cycles ago. The second draft comments that got those tables into Annex B were exactly that....the load calcs are so conservative that this is not a real world issue when loads are calculated per Article 220.I've never had a problem with using the standard calculations because the NEC load calcs. are so conservative.