When is the Neher and McGraft required to be used for 480V buried circuits? Is it limited to concrete encased ducts only? Does it apply to ducts in direct buried without concrete?
Whether it is "required" is a bit of an interpretation for the designer.The Neher McGrath calculation method can be used for any underground installation. But I believe it is never "required." There are other methods of determining ampacity. Two notes:
1. If you wish to use this method, the calculation must be performed by, and sealed by, a licensed Professional Engineer.
2. My memory of past attempts to use this method tells me that it will generally give you a lower ampacity value than the NEC tables. There is sometimes a question as to whether the tables can be used in a given situation.
Out of curiosity, may I ask whether you are already using this method, and if so, how? Or is your concern that you may be required to use it for a project, but you don't know how to use it?When is the Neher and McGraft required . . . ?