I am performing duct bank calculations on a 480V feeder with THWN conductors. I’d expect I may utilize the 90C rating for de-rate calculations, as long as it is not less than the 75C rating ampacity to maintain termination ratings.
However, I ran into an article that speaks to 100% rated circuit breaker assemblies... which is what I have. Does this hold any weight? I suspect not.
“There is typically some discussion about utilizing the 90 C rating of the conductors. NEC Section 110.14 (C) states: “Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustments, corrections or both.” This application typically isn’t applicable for 100% rated breakers, where, in fact, 90 C cable is required. But it must be sized per the 75 C ampacity. These 100% rated breakers use the wire as a heat sync to serve continuous loads at the full rating of the breaker.”
https://www.csemag.com/articles/heating-calculations-for-electrical-duct-bank/
However, I ran into an article that speaks to 100% rated circuit breaker assemblies... which is what I have. Does this hold any weight? I suspect not.
“There is typically some discussion about utilizing the 90 C rating of the conductors. NEC Section 110.14 (C) states: “Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustments, corrections or both.” This application typically isn’t applicable for 100% rated breakers, where, in fact, 90 C cable is required. But it must be sized per the 75 C ampacity. These 100% rated breakers use the wire as a heat sync to serve continuous loads at the full rating of the breaker.”
https://www.csemag.com/articles/heating-calculations-for-electrical-duct-bank/