I've almost always determined cable ampacity straight from table 310.15(B)16 - the standard 3 conductors in a conduit table. Even for underground runs with more than one conduit (aka - a duct bank).
But most of our projects usually only have 2 or 3 parallel conduits, so that usually seems reasonable, and it seems to be allowed by the NEC per 310.15(A)(1):
And the NEC handbook even states that when using the load calcs. in section 220, table 310.15(A)(1) values are usually sufficient. I also have a lot of reference drawings from other engineers and firms come across my desk. I don't think I have ever seen drawings where someone went to the "engineering supervision" section and used the Neher Mcgrath tables in Appendix B.
But now I have a 2500 amp duct bank, and I'm considering applying some de-rating for multiple conduits instead of simply using 6 sets of 600KCM.
Any thoughts on this? Is de-rating for multiple conduits necessary?
If I do de-rate, the problem I run into, is that according to appendix B, even 9 conduits with 500KCM wire is only good for 2160 amps. And the only details don't really show any higher ampacity situations. Any detailsshown for more than 9 conduits only include one conductor per conduit. So I have no idea how to get to 2500 amps without having to buy special software.
But most of our projects usually only have 2 or 3 parallel conduits, so that usually seems reasonable, and it seems to be allowed by the NEC per 310.15(A)(1):
Code:
[COLOR=#000000][FONT="][B](1) Tables or Engineering Supervision.[/B][/FONT][/COLOR][COLOR=#000000][FONT="] [/FONT][/COLOR][COLOR=#000000][FONT="]Ampacities for conductors shall be permitted to be determined by tables as provided in [URL="http://www.madcad.com/library/182159/557186/#nfc_70_2014_ID000070040804"]310.15(B)[/URL] or under engineering supervision, as provided in [URL="http://www.madcad.com/library/182159/557186/#nfc_70_2014_ID000070037860"]310.15(C)[/URL].[/FONT][/COLOR]
And the NEC handbook even states that when using the load calcs. in section 220, table 310.15(A)(1) values are usually sufficient. I also have a lot of reference drawings from other engineers and firms come across my desk. I don't think I have ever seen drawings where someone went to the "engineering supervision" section and used the Neher Mcgrath tables in Appendix B.
But now I have a 2500 amp duct bank, and I'm considering applying some de-rating for multiple conduits instead of simply using 6 sets of 600KCM.
Any thoughts on this? Is de-rating for multiple conduits necessary?
If I do de-rate, the problem I run into, is that according to appendix B, even 9 conduits with 500KCM wire is only good for 2160 amps. And the only details don't really show any higher ampacity situations. Any detailsshown for more than 9 conduits only include one conductor per conduit. So I have no idea how to get to 2500 amps without having to buy special software.