• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

NEMA-2 or NEMA-3R Transformer beside sink?

Merry Christmas

elecshop

Member
Location
FL, USA
Occupation
Electrical Engineer
I have a 112.5kVA 3PH 4W 480V transformer located 3' from the edge of a sink, indoors, in a commercial space in the back-of-house in a restaurant space.
Is NEMA-2 enclosure sufficient, or it needs NEMA-3R?
I know that NEMA-2 protects against falling dirt and minor amounts of falling non-corrosive liquids/water in indoor environments.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I wouldn't worry about it at all. For most small dry-type transformers, like this example, the difference between an indoor and outdoor installation is the field addition of 'weathershields' which prevent rain from being blown into the enclosure.
 