jcorbin
- romney,wv,usa
I have a spec which calls for rigid conduit, aluminum is not allowed., and then it calls for nema 4 cast metal type outlet boxes and conduit fittings see spec below
2.02 OUTLET BOXES
A. Outlet boxes for concealed work shall be zinc-coated or cadmium-plated sheet steel boxes
suitable for the service and type outlet (device) installed. Outlet boxes and conduit fittings for
outdoor work and exposed interior work shall be NEMA 4 cast-metal type with threaded hubs for
conduit entrance. Boxes and conduit fittings for outdoor work shall have gasketed cover plates.
Plastic boxes and cast "white metal" boxes classified as NEMA 4 will not be acceptable.
B. All outlet boxes used for supporting fixtures shall be furnished with malleable iron fixture
studs of "no-bolt" type secured by locknut.
C. All boxes, whether outlet, junction, pull, or equipment, shall be furnished with appropriate
covers What is a nema 4 outlet box? or conduit fitting. Is the engineer referring to cast aluminum devise boxes or the malleable type. He goes on in paragraph B to indicate a malleable type box for fixure hanging. Big difference in price! I am not sure what a nema 4 outlet box is. Please advise Jody Corb
			2.02 OUTLET BOXES