Hi everyone,
I started to order an HMI terminal today but ran into a problem.
While the HMI Terminal is rated NEMA 4, Its electrical rating is general purpose, ie. no Class or div rating.
This is how i currently understand things.
The NEMA 4 rating means that the enclosure and seal of the hmi display is rated for hose directed water to obtain the maximum seal. Its also oil,dustight.
The Class / Div rating is used to rate the electrical characteristics of the HMI in regards to its use in certain areas. For example, an HMI rated for class 1 div 2, class 2 div 2 groups efg means that the HMI can be safely used in class 1 / div 2 locations and also class 2 / div 2 group efg locations when the installation methods for the HMI is properly done and as well as using correct electrical installation methods are used for the wiring.
This does not mean that the HMI terminal with the NEMA 4 rating is acceptable for use in a class 1 div 2, or class 2 div 2 environment (this is where the unit was to be placed). There will be an accumulation of dust on the HMI enclosure.
Please comment, I don't want to walk into my meeting later this week and be incorrect. This plant is trying to overcome some of the previous electrical installation practices (any thing goes). They want to do the right thing, but several of the engineers of the anything goes age are still there and may fight me on this. I want to be able to present the facts and back it up with the correct rules.
Thanks in advance,
James
I started to order an HMI terminal today but ran into a problem.
While the HMI Terminal is rated NEMA 4, Its electrical rating is general purpose, ie. no Class or div rating.
This is how i currently understand things.
The NEMA 4 rating means that the enclosure and seal of the hmi display is rated for hose directed water to obtain the maximum seal. Its also oil,dustight.
The Class / Div rating is used to rate the electrical characteristics of the HMI in regards to its use in certain areas. For example, an HMI rated for class 1 div 2, class 2 div 2 groups efg means that the HMI can be safely used in class 1 / div 2 locations and also class 2 / div 2 group efg locations when the installation methods for the HMI is properly done and as well as using correct electrical installation methods are used for the wiring.
This does not mean that the HMI terminal with the NEMA 4 rating is acceptable for use in a class 1 div 2, or class 2 div 2 environment (this is where the unit was to be placed). There will be an accumulation of dust on the HMI enclosure.
Please comment, I don't want to walk into my meeting later this week and be incorrect. This plant is trying to overcome some of the previous electrical installation practices (any thing goes). They want to do the right thing, but several of the engineers of the anything goes age are still there and may fight me on this. I want to be able to present the facts and back it up with the correct rules.
Thanks in advance,
James