Hi Everyone,

Dose anyone know where in the 2008 NEC it talks about NEMA in Enclosures and/or boxes? More specifically talking about NEMA boxes and motors.

Thanks,

Daniel
 

bphgravity

Senior Member
Location
Florida
Check out Section 110.20 of the 2008 NEC. The enclosure-type numbers are from NEMA. The section and table was moved from 430.91 in the 2005 NEC.
 

Carultch

Senior Member
Location
Massachusetts
Hi Everyone,

Dose anyone know where in the 2008 NEC it talks about NEMA in Enclosures and/or boxes? More specifically talking about NEMA boxes and motors.

Thanks,

Daniel

NEMA enclosure ratings are described here:
https://www.nema.org/Products/Documents/nema-enclosure-types.pdf

Executive summary:
NEMA1 = indoors
NEMA3R = outdoors and in a specific orientation, usually upright
NEMA4 = outdoors and in any orientation
NEMA4X= like NEMA4, but also rust proof
 

kwired

Electron manager
Location
NE Nebraska
Check out Section 110.20 of the 2008 NEC. The enclosure-type numbers are from NEMA. The section and table was moved from 430.91 in the 2005 NEC.
Did you mean 110.28? Maybe it was moved since 2008, 110.28 in 2014 does have table like you described, and sounds like what OP may be looking for.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Did you mean 110.28? Maybe it was moved since 2008, 110.28 in 2014 does have table like you described, and sounds like what OP may be looking for.
Since the OP asked the question specifically for the 2008 cycle, Bryan answered with the correct section number and it was 110.20.

Roger
 