A NEMA L5-30R recept is rated for 125v, 2 pole, 3 wiring grounding. Does this not mean that a 2 pole breaker needs to installed for it?
A contractor wired the rect for 208v since he saw the 2 poles on the panel schedule and the UPS that was supposed to use the L5-30 got fried when they plugged it in. A L5-30 was specifically called for on design plans.
A contractor wired the rect for 208v since he saw the 2 poles on the panel schedule and the UPS that was supposed to use the L5-30 got fried when they plugged it in. A L5-30 was specifically called for on design plans.