NEMA Rated Type 3 All-Weather Sigma 1420 single outlet box

Status
Not open for further replies.

msantelia

Member
Location
Texas
Occupation
Commercial and Residential Real Estate
Can you splice and extend a Hayward ColorLogic 80/40 cord from within a NEMA Rated Type 3 All-Weather Sigma 1420 single outlet box place at grade level, in the path of water runoff, to an elevated junction drive box? An electrician we used did this and I have argued this violates Hayward manufacturing and NEMA ratings for a box that will be exposed to running water over it. https://1drv.ms/u/s!ArY2guv0I7FOiOYAw41GnLAs5j0Gmw?e=8VkFJc
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Violating the manufacture's instructions violates NEC Section 110.3(B). Assuming the box is only marked one of the Type 3 series (R, S, X, RX, or SX) violates Section 110.28 as you have described the installation. See Table 110.28.

I moved this to a Forum where it is likely to get better exposure. (It isn't relevant to Hazardous Locations)
 

msantelia

Member
Location
Texas
Occupation
Commercial and Residential Real Estate
Violating the manufacture's instructions violates NEC Section 110.3(B). Assuming the box is only marked one of the Type 3 series (R, S, X, RX, or SX) violates Section 110.28 as you have described the installation. See Table 110.28.

I moved this to a Forum where it is likely to get better exposure. (It isn't relevant to Hazardous Locations)
The box and cover were rated 3R. Based on the placement it should be at least Type six. Much appreciated!
 

kwired

Electron manager
Location
NE Nebraska
Does water just "run over it" or does it become "submerged" on somewhat regular basis?

I'd be drilling weep holes as condensation seems to happen within no matter how much you try to avoid it. If submersion is an issue then it simply needs elevated to above highest expected water level.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC

kwired

Electron manager
Location
NE Nebraska
I don't see what the problem is, it's LV landscape or pool lighting wiring from the driver to the heads. I also don't know where the OP gets his information from either. That cable is rated for direct burial.

My recommendation is to use gel filled wire nuts and a new cover and gasket. Doesn't matter what you do, you are always going to have moisture in there.


-Hal
He said it is at grade level and in the path of water runoff, which prompted me to ask for more details. It possibly could be submerged according to what he said then it possibly should be N6 instead of 3 or 3R, or moved to where it won't be submerged.
 