We have quite a few cord and plug attached pieces of small equipment in the building that are using the NEMA L19-20, 4 pole, 4 wire, non-grounding plugs, but are NOT utilizing the single phase 277v component of the plug in their operation. They are strictly 480, 3 phase in operation, even though the 277v single phase is available in our facility system. My contention is that this is a mis-use of this configuration and not code compliant. I think we should be using the L16-20 configuration, which is for 480 v, three phase, w/ground.
Am I correct that this is an illegal use of this configuration and they should all be changed out where applicable? I just replaced one yesterday which said not to use the locking lug as ground, neutral only. Brought it to the super's attention, but he didn't seem willing to comment.