kingpb
- SE USA as far as you can go
- Engineer, Registered
Last week I attended a dog and pony show sponsored by Schneider Electric, (SquareD) with the advertised topic of intelligent motor control centers. Without all the boring details, it was not what I thought it was going to be. However, it did give me the opportunity to ask them about the push using IEC contactors in starters.
The following is my interpretation/paraphrase of the conversation:
Q1: It seems that IEC starters are showing up more frequently as new equipment and as replacements. Since the methods of calculating the short circuit currents is different for IEEE and IEC devices, how are you rating the IEC equipment?
A1: We agree that IEEE and IEC calculation methods are different and therefore the ratings do not mean the same thing, because the short circuit values mean different things.
Q2: Then how are IEC devices being provided in lieu of NEMA devices, or as replacements, especially since there is no cross reference between the two?
A2: IEC devices come in many more sizes then the NEMA sizes and therefore you will end up with an IEC starter that is larger, maybe two sizes, then what you would get with a NEMA starter.
Q3: Even if the starter is two sizes larger, how do you know it has the short circuit rating capable of handling the IEEE calculated current?
A3: We have performed factory tests to see if they will carry the fault current, but we do not go so far as to provide dual rating nameplates. But our technical folks can help with sizing and providing an appropriate IEC size.
Q4: So in essence there is a false sense of security being provided that it won't blow up if a fault occurs. So unless someone performs the IEC 60909 calculations you don't know what the proper rating is.
A4: If your replacing NEMA starters/contactors then you should stay with NEMA devices, and shouldn't mix them. Unfortunately, because the market is so competitive, if the specification does not preclude IEC devices, then that is what we will quote, because they cost less.
All I can say, is buyer beware. If the device you are replacing is a NEMA device, then that is what it should be replaced with, unless someone has performed the appropriate IEC 60909 calculations. Anyone your talking too, ask them if they are aware of the differences in calculation methods. If they give you a blank stare, or can't specifically tell you what or why it is different, then replace according to the method used for determining the ratings. Saving a few bucks using IEC devices instead of NEMA could unknowingly be putting someones safety at risk. I don't want that on my conscience, and I'm sure none of you do either.