cripple
Senior Member
- Location
- Santa Fe, New Mexico
I have an electrical design which shows a pad with a utility transformer and a customer owned distribution switchboard. The grounding detail shows the utility transformer and the switchboard neutral (grounded) conductor being grounded to same concrete encased electrode in the pad. I told the design engineer that I did not think this met Code, because the grounding electrode system would be paralleled with the neutral between the utility transformer and the switchboard. His response was, the utility transformer is required by the NESC to be grounded, and NEC requirements did not apply. This is my first installation with the utility transformer and the customer owned equipment being placed on the same pad. Any comments?