For a 1250KW 13.8kv 0.8P.F, how do you size the generator neutral grounding transformer? how do you size grounding resistor across the secondary of the grounding transformer? Details appreciated. Thanks in advance.
This is interesting. My first reaction is would this be 250 compliant?Avtron Neutral Grounding Resistors are designed to provide added safety to industrial distribution systems by limiting ground fault current to reasonable levels. In a typical solidly grounded three phase system, the neutral is tied directly to earth ground. This can cause high ground fault current (typically 10,000 to 20,000 amps) and excessive damage to transformers, generators, motors, wiring, and associated equipment. Inserting an Avtron Neutral Grounding Resistor between neutral and ground limits fault current to a safe level (typically 25 to 400 amps) while still allowing sufficient current flow to operate fault clearing relays.
A current transformer in the grounding line provides signal to the relay protection of the generator. On the other, hand the resistor in the grounding circuit limits the ground fault.For a 1250KW 13.8kv 0.8P.F, how do you size the generator neutral grounding transformer? how do you size grounding resistor across the secondary of the grounding transformer? Details appreciated. Thanks in advance.