ElectricianJeff
Senior Member
- Location
- Southern Illinois
I went on a service call yesterday. The HO said that Saturday his wife came home and when she turned on the lights in the kitchen the ceiling fan bulb blew and all the ceiling lights in the house went dim and remained that way.
This is a 1920's 1 1/2 story. It has a 15 year old 200 amp. service. Initially, I figured this was a classic case of a lost neutral. I started by checking all the connections in the main panel, everything was tight. I also found it odd that two circuits were effected by this condition, one circuit fed the ceiling lights on the main level and the other fed the ceiling lights and a bathroom recep. on the 2nd level. Both of these circuits where on the same leg in the panel, and were the old cloth covered 2 wire romex. I checked the entrance conductors and all the circuits under load and had 125V to neutral everywhere. I pulled out the affected breaker to inspect the buss bar and discovered in the process "ouch" that I had 125 Volts to grounds on the disconnected conductor when the other breaker was on. This condition went away when the other breaker was opened.
I moved one of the breakers to the other leg in the panel and had 240V at the lights, real bright, and I read 240V at the recep in the bathroom when both circuits were closed.
I went into the attic to inspect the wiring above the ceiling fan in the kitchen and found a real rats nest. I wish I had taken a picture. There where about 6 conductors wire nuted together there, no box just flying splices everywhere. I showed this to the HO and he said he had a "electrician" friend work on this about 10 years ago.
I was beginning two run out of time so I saw a suspicious splice into the neutral of the old knob and tube wiring. I cut it and backfeed the wire from a known good neutral from an extension cord. The lights on the main level returned to normal operation. Lights where still dim on the second floor. I checked the recep in the bathroom at 125V but it dropped to around 50V under the load of a small space heater. Again pointing to a lost neutral.
I am going back Friday. I told the HO that the first thing I was going to do was to cleanup the mess above the kitchen and hopefully discover the problem in that process.
I got to thinking about this having read posts on here about "California 3ways" which I don't believe I have ever encountered in the field. I still don't understand why 2 circuits are affected by this condition unless the 3-way in the kitchen is being supplied by both these circuits.
Sorry about the long post but I'm curious if anyone has experienced a similar situation and can shed some light on the outcome.
This is a 1920's 1 1/2 story. It has a 15 year old 200 amp. service. Initially, I figured this was a classic case of a lost neutral. I started by checking all the connections in the main panel, everything was tight. I also found it odd that two circuits were effected by this condition, one circuit fed the ceiling lights on the main level and the other fed the ceiling lights and a bathroom recep. on the 2nd level. Both of these circuits where on the same leg in the panel, and were the old cloth covered 2 wire romex. I checked the entrance conductors and all the circuits under load and had 125V to neutral everywhere. I pulled out the affected breaker to inspect the buss bar and discovered in the process "ouch" that I had 125 Volts to grounds on the disconnected conductor when the other breaker was on. This condition went away when the other breaker was opened.
I moved one of the breakers to the other leg in the panel and had 240V at the lights, real bright, and I read 240V at the recep in the bathroom when both circuits were closed.
I went into the attic to inspect the wiring above the ceiling fan in the kitchen and found a real rats nest. I wish I had taken a picture. There where about 6 conductors wire nuted together there, no box just flying splices everywhere. I showed this to the HO and he said he had a "electrician" friend work on this about 10 years ago.
I was beginning two run out of time so I saw a suspicious splice into the neutral of the old knob and tube wiring. I cut it and backfeed the wire from a known good neutral from an extension cord. The lights on the main level returned to normal operation. Lights where still dim on the second floor. I checked the recep in the bathroom at 125V but it dropped to around 50V under the load of a small space heater. Again pointing to a lost neutral.
I am going back Friday. I told the HO that the first thing I was going to do was to cleanup the mess above the kitchen and hopefully discover the problem in that process.
I got to thinking about this having read posts on here about "California 3ways" which I don't believe I have ever encountered in the field. I still don't understand why 2 circuits are affected by this condition unless the 3-way in the kitchen is being supplied by both these circuits.
Sorry about the long post but I'm curious if anyone has experienced a similar situation and can shed some light on the outcome.