In an on-line article for EC&M magazine, Mike Holt shows a Figure with
L!, L2, N and calculates the neutral current to be equal to the current
in either one of the balanced 2-phase wires. The reference is to
"NEC 220.22.
I don't find this article in NEC.
I don't understand how this can be applied to a HVAC unit , say
208-1 Ph., with equal phase loading, with the load equipment
providing terminals for L1, L2, and GND.? (no neutral wire)