Was it ever ok with the nec for the neutrals and egc to be under the same lug in panelboard ? If so when ?
It was done, but in ignorance. Panels were notorious for not having enough space for neutrals and EGs. EG bars were special order. That hasn’t been a problem for quite some time though.Was it ever ok with the nec for the neutrals and egc to be under the same lug in panelboard ? If so when ?
That is when the wording was added to the NEC, it was a UL listing requirement for the panelboard for decades before that.Looks like that came into play 1990 NEC 384-20 and currently 408.41
Yes I am aware of that thank you. I was simply adding to the conversation as to when it was added to the NEC if anyone was interested.That is when the wording was added to the NEC, it was a UL listing requirement for the panelboard for decades before that.
Nor looked for underlying implications of multiple neutral taps. Seen many old panels that were such a mess, (certainly handiman hack job) determining with even a mild certainty a single complete circuit was almost impossible. And compounding that was multiple neutral under single screw lug, and then try to find the second circuit to shut down to safely remove the one with the panel in that condition. One such one, recently opened cover and couldn't be sure there even was a neutral bus to look at the mess, and that was without any AFCI/GFCI pigtails.Most of us didn't have any idea what UL required.