why it is not acceptable to have multiple pathes for neutral current[objectional current]?

What objectionable current do you have in mind? There are instances where the NEC permits neutral current to flow on other metallic paths.
 
Another reason why you want to try and eliminate objectionable current, a fire hazard:

1113845784_2.jpg
 
Say current is flowing on a piece of emt and you touch the emt and another grounded object. Does that answer the question? :)
As long as the EMT is a parallel path, that will never be a shock hazard. The only votlage available to drive a shock would the the voltage drop on the parallel paths. The addition of a parallel path reduces this voltage drop.
 
Another reason why you want to try and eliminate objectionable current, a fire hazard:

1113845784_2.jpg

As long as the conduit is a parallel path and not the only path I don't see any way there would be enough current flow to cause a temperature rise at a loose conduit fitting.
 
As long as the EMT is a parallel path, that will never be a shock hazard. The only votlage available to drive a shock would the the voltage drop on the parallel paths. The addition of a parallel path reduces this voltage drop.
Interesting so the only reason that objection current is not wanted is ?????
 
As long as the conduit is a parallel path and not the only path I don't see any way there would be enough current flow to cause a temperature rise at a loose conduit fitting.

Agreed, but that graphic depicts what would happen when the neutral is disconnected.
 
why it is not acceptable to have multiple pathes for neutral current[objectional current]?

(edited to add) Adding to comments already made.

Did my best to delete most of the rant.

I don't like MGN, but not for most of the reasons stated here.

First lets look at the regulation (NEC primarily):
Let's start with, Which side of the disconnect are you on?
If you are on the utilty side then grouding the neutral well and often is good and proper.
But on our side of the disconnect, grounding the neutral once is the only safe way.
Unless the system is over 100V, the MGN is again good.

Okay that doesn't make any sense.

Installation specifics:
Most conventional wisdom says that current over the grounding path is dangerous. Humm ... Most arguments are about loose connections, or loose fittings. I'll agree if the connections are poor there will be problems - but that is true MGN or SPG (single point ground)

Lets look at the case of current over a conduit (because of and MGN) - and one is holding the conduit and also touching a grounded object:
Well, if the conduit is bonded as it should be, I say there is no potential difference between the conduit and the ground - so no hazard. Ahhh, but what if the conduit is not bonded as it should be? Well, then the person doing the touching is toast (okay, gets shocked - maybe not dead). What happens if the system is SPG as it should be and the conduit is not bonded as it should be and there is a fault? The person doing the touching is again toasted - likely worse than the above example.

So, why is MGN on our side of the disconnect not acceptable? Cause the code says it's not.

Are there other reasons? Yes, I think so. But we Americans would have to ditch our entire concept of grounding the neutral at residences. And we would have to convice the utilities to drive their own darned ground rods - or give up their concept on MGN.