A service entrance has a 3 phase, 4 wire circuit from a 480/277 V transformer. The service entrance has a 3 phase, 3 wire feeder to a panelboard where 80% of the load is made up of VFD's for 3 phase motors. Per NEC 310.15(B)(5) the 3 phase, 4 wire circuit to the service entrance is primarily loaded with non-linear loads. According to the code, wouldn't the service entrance conductors result in 4 CCC's in the conduit?
From what I understand, VFD's produce very little triplen harmonics. The 5th, 7th, 11th, 13th harmonics do not result in neutral current. Does the code address this anywhere and provide exceptions to not count the neutral as a CCC? For example, using active harmonic filters.