Q. On a 1,600A 277/480V service, is the neutral conductor from the utility transformer to the service disconnect considered a current carrying conductor if the only line-to-neutral loads is a 200A lighting panel supplying non-linear loads?
A. The neutral (grounded) service conductor for this installation is considered a current carrying conductor for conductor ampacity adjustment purposes because a major portion of the load consists of nonlinear loads [310.15(B)(2)(a) and 310.15(B)(4)(c)].
My Response to Mike was:
You say that the neutral is a current carring conductor because a major portion of the load consists of nonlinear loads [310.15(B)(2)(a) and 310.15(B)(4)(c)].
I would, based on the information supplied, disagree . I would say that since the main is 1600 amps, the load shown in the question below is not the only load on the main. Therefore the 200 amp load shown may be very small and not a major portion of the load on the main switch.
Mike's Response :
If the 200A is 100% of the total neutral load, then it's a major portion. This conductor is 100% loaded with nonlinear loads. It's not the % of load based on the ungrounded conductors. The issue is heat and a 100% loaded conductor (sized 4x smaller) is still a heat generating conductor
Q. On a 1,600A 277/480V service, is the neutral conductor from the utility transformer to the service disconnect considered a current carrying conductor if the only line-to-neutral loads is a 200A lighting panel supplying non-linear loads?
A. The neutral (grounded) service conductor for this installation is considered a current carrying conductor for conductor ampacity adjustment purposes because a major portion of the load consists of nonlinear loads [310.15(B)(2)(a) and 310.15(B)(4)(c)].
My Response to Mike was:
You say that the neutral is a current carring conductor because a major portion of the load consists of nonlinear loads [310.15(B)(2)(a) and 310.15(B)(4)(c)].
I would, based on the information supplied, disagree . I would say that since the main is 1600 amps, the load shown in the question below is not the only load on the main. Therefore the 200 amp load shown may be very small and not a major portion of the load on the main switch.
Mike's Response :
If the 200A is 100% of the total neutral load, then it's a major portion. This conductor is 100% loaded with nonlinear loads. It's not the % of load based on the ungrounded conductors. The issue is heat and a 100% loaded conductor (sized 4x smaller) is still a heat generating conductor