I think I may have found an error in a test question help appreciated.
The neutral conductor that carries only the unbalanced current from a 3 wire delta circuit or 4 wire three phase wye circuit is considered a current carrying conductor for the purpose of table 310.15(b)(3)(a) .
I would say true, answer key says false stating 310.15(B)(5)(a) which I think refers to single phase. My point is
The neutral conductor that carries only the unbalanced current from a 3 wire delta circuit or 4 wire three phase wye circuit is considered a current carrying conductor for the purpose of table 310.15(b)(3)(a) .
I would say true, answer key says false stating 310.15(B)(5)(a) which I think refers to single phase. My point is
310.15(B)(5)(b) basically there will be neutral current so it should be counted?