denders
Member
- Location
- Allentown, PA, USA
Hello folks,
I'm asking whether the neutral conductors between the transformer and service entrance switchboard are current carrying conductors for deciding whether the conductors should be derated.
1. The transformer secondary is 480VAC Wye.
2. There are multiple sets of secondary conductors. 4 Wire, 3 phases plus neutral.
3. The switchboard is the service entrance. The neutral is grounded in the switchboard.
4. There are multiple 480VAC 3 phase loads (motors, etc.). Not to muddy the waters, but some motors are on VFDs, nothing larger than 30 HP.
5. Also various 480/240/120 transformers for other loads.
6. There are also single phase 277VAC loads, Lighting (LED) and Heat tracing.
7. The various loads will probably change over the life of this facility.
If you don't mind, I'd like a bit more of an answer than Yes or No.
Thanks
Dave
I'm asking whether the neutral conductors between the transformer and service entrance switchboard are current carrying conductors for deciding whether the conductors should be derated.
1. The transformer secondary is 480VAC Wye.
2. There are multiple sets of secondary conductors. 4 Wire, 3 phases plus neutral.
3. The switchboard is the service entrance. The neutral is grounded in the switchboard.
4. There are multiple 480VAC 3 phase loads (motors, etc.). Not to muddy the waters, but some motors are on VFDs, nothing larger than 30 HP.
5. Also various 480/240/120 transformers for other loads.
6. There are also single phase 277VAC loads, Lighting (LED) and Heat tracing.
7. The various loads will probably change over the life of this facility.
If you don't mind, I'd like a bit more of an answer than Yes or No.
Thanks
Dave