Neutral at 3-Way Switch

Status
Not open for further replies.

JRC

New User
Location
New Jersey
Occupation
Engineer
I am installing a new light at the bottom of a basement stairway. I plan on bring power from the panel to the 1st switch. From the 1st switch, I will run a 14-2 to the light. Also from the 1st switch, I will run a 14-3 to the 2nd switch but will wrap black tape around the white wire indicating that it is no longer neutral. Is this per code? I have seen statements before indicating that per a recent code change, a neutral wire must be present at every switch, even if it is not connected.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
The requirement to reidentify the grounded conductor as ungrounded is not a recent change, its been a requirement for about 15 or more years
 