Just would like to have a discussion and get some thoughts/answers to grounded conductor at switch 2014 NEC requirement. 404.2 (C) also 200.7 (C) (1)
I'm looking at. 404.2 (C) at end of the paragraph referring to where a grounded conductor is required says "for other than the following" 404.2 (C) (4) Says "where a switch does not serve a habitable room or bathroom." Does this mean a grounded conductor is only required for bedrooms and bathrooms?
404.2 (C) (5) " where multiple switch locations control the same lighting load such that the entire floor area of the room or space is visible from the single or combined switch locations." I read this as a 3 or for way switched does not need a grounded conductor at all locations if all lighting outlets are visible from each switch location? Going back to 404.2 (C) a grounded conductor would not be required for say a stairway 3 way both up and downstairs or at the switch for a garbage disposal?
Thanks for any replies this is a topic with my crew at work right now, a Master was sent to work with our crew for the day, he dropped a 3 wire down to the switch in the garage where the light is powered at the light, I asked if he did this because the neutral is required at the switch he answered it is not required just good practice. I being a new hire JW and also holding an RW replied its nice to have a neutral at the switch if needed. Many apprentices I work with are being taught not to power and switch a 3 way from the same end because their wireman believes red and white travelers are illegal I point out 200.7 (C) (1) allows the white to be reidentified they then say well you need a neutral at all switch locations. I just would like to be 100% NEC compliant when talking and teaching. Thanks
I'm looking at. 404.2 (C) at end of the paragraph referring to where a grounded conductor is required says "for other than the following" 404.2 (C) (4) Says "where a switch does not serve a habitable room or bathroom." Does this mean a grounded conductor is only required for bedrooms and bathrooms?
404.2 (C) (5) " where multiple switch locations control the same lighting load such that the entire floor area of the room or space is visible from the single or combined switch locations." I read this as a 3 or for way switched does not need a grounded conductor at all locations if all lighting outlets are visible from each switch location? Going back to 404.2 (C) a grounded conductor would not be required for say a stairway 3 way both up and downstairs or at the switch for a garbage disposal?
Thanks for any replies this is a topic with my crew at work right now, a Master was sent to work with our crew for the day, he dropped a 3 wire down to the switch in the garage where the light is powered at the light, I asked if he did this because the neutral is required at the switch he answered it is not required just good practice. I being a new hire JW and also holding an RW replied its nice to have a neutral at the switch if needed. Many apprentices I work with are being taught not to power and switch a 3 way from the same end because their wireman believes red and white travelers are illegal I point out 200.7 (C) (1) allows the white to be reidentified they then say well you need a neutral at all switch locations. I just would like to be 100% NEC compliant when talking and teaching. Thanks