neutral balanced or not
infinity
New Jersey
Journeyman Electrician
What do you mean by a 4-wire MWBC? Three circuits sharing one neutral on a 3? system? The neutral would carry some current unless all three loads were exactly the same. For example 3-100 watt lamps on a 4 wire MWBC fed from a 208Y/120 volt system would have 0 amps of neutral current. If one lamp burnt out the neutral current would be approximately equal to the current on the ungrounded conductors.
charlie b
Lockport, IL
Semi-Retired Electrical Engineer
The neutral current can be calculated from the following formula, with a, B, C, and N representing the currents in the three phases and the neutral, and with "A2" meaning "A squared":
N = SQRT ( A2 + B2 + C2 -AB -AC -BC).
Try this formula with equal values of A, B, and C, and you will discover that the neutral current calculates out to zero.
Smart $
Esteemed Member
Ohio
Note the result of the above formula is only accurate for loads having equal power factor.