randolph wiggins said:
should the neutral in panel 120v have aground on neutral bar

Welcome to the Forum. If I understand your question you might want to look at 250.92. If that doesn't help please provide more details of the install in question.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
randolph wiggins said:
should the neutral in panel 120v have aground on neutral bar

Hey randolph-- if the panel is the main panel then the grounded conductors (neutrals- if you must) and the grounds will be connected together. Once they leave that panel they are separate.
 