Neutral Bonding on 480/277V Lighting Panel

Status
Not open for further replies.

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
It does not matter whether this is a lighting panel or whether it serves HVAC equipment. It also does not matter whether it is 480/277 volts or 120/208 volts. If there is a panel upstream (i.e., this is not the first panel that is connected to a transformer secondary), then its N and G bars must not be connected to each other.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
When you say '4-wire breaker' you're being very unclear. Presumably you should be saying '4-wire feed', since there aren't many systems where 4 wires go to the breaker. Beyond that, do these 4 wires consist of 3 hots and a neutral, or 2 hots, 1 neutral, and 1 ground? If the former, you'd better have some other form of ground, such as metal conduit. In any case I agree with the previous post: no, you don't bond the neutral.
 