What is the amperage of a neutral bus bar that is .5" × 4" I have searched through the NEC book and cannot find the formula anywhere.
Such terminal bars do not have a current rating. If the wire fits, you are good. Now if you retrofit a lug to that bar that is not supplied/approved by the bar maker, you could be called on a 110.3 (B).
What is the amperage of a neutral bus bar that is .5" × 4" I have searched through the NEC book and cannot find the formula anywhere.
Listed connections to aluminum or copper busbars not
smaller than 6 mm thick × 50 mm wide (1∕4 in. thick × 2 in.
wide) and of sufficient length to accommodate the
number of terminations necessary for the installation. If
aluminum busbars are used, the installation shall also
comply with 250.64(A).
Wouldn't a neutral bus bar in several sections of switchgear need to be large enough to carry the load?
Take a look here:
http://forums.mikeholt.com/showthread.php?t=189514&highlight=copper
Rob, I am aware of those common 750/1000 figures for ampacity of busbars, bit IIRC the nec doesn't really have provisions for allowing us to make/use/calculate the ampacity of a busbar right?
As a rough and ready rule of thumb we worked on 1000A per square inch.What is the amperage of a neutral bus bar that is .5" × 4" I have searched through the NEC book and cannot find the formula anywhere.
The neutral must be sized for the load so I would think the busbar would also. 210.19 I think
What is the amperage of a neutral bus bar that is .5" × 4" I have searched through the NEC book and cannot find the formula anywhere.
This question was asked on a master electrician pre-test